[Check_mk (english)] Agent for MODBUS

Hi!

I want to monitor our mitsubishi air conditioning system via modbus. How do I activate the modbus from check_mk/share/treasures/modbus? What file has to be copied to which location? I am using v1.2.8p22.

Hi Dirk,

first you should test if the agent_modbus is working with your device.

If this is working then you should copy the other files in the shown directories under your local structure in your site.

checks → share/check_mk/checks

modbus_value → share/check_mk/checks

wato → share/check_mk/web/plugins/wato

perfometer and checkman are not important for testing

If all went the right way you should find a new rule inside “Datasource programs”.

Best regards

Andreas

···

Riemekasten Dirk DRiemekasten@natus.de schrieb am Di., 23. Mai 2017 um 16:03 Uhr:

Hi!

I want to monitor our mitsubishi air conditioning system via modbus. How do I activate the modbus from check_mk/share/treasures/modbus? What file has to be copied to which location? I am using v1.2.8p22.

–

Mit freundlichen GrĂĽĂźen /

With best regards

i. A. Dirk Riemekasten

IT-Administrator

NATUS GmbH & Co. KG

Loebstr. 12

54292 Trier

Germany

phone: +49(0)651/1449-243

fax: +49(0)651/1449-7243

e-mail:
driemekasten@natus.de

web:
www.natus.de

NATUS GmbH & Co.
KG, Elektrotechnische Spezialfabrik fĂĽr Industrie-Schaltanlagen-Systeme

HRA 2733 | USt.-IdNr.: DE 149 792 966 | Persönlich haftende Gesellschafterin:

NATUS Gesellschaft mit beschränkter Haftung | Amtsgericht Wittlich | HRB 1302

Geschäftsführer: Frank Natus


checkmk-en mailing list

checkmk-en@lists.mathias-kettner.de

http://lists.mathias-kettner.de/mailman/listinfo/checkmk-en

Hi Andreas,

testing on the shell with „./agent_modbus 10.10.8.122 502 5:1:gauge:act_temp1“ is reading the correct value. After copying the files
you mentioned to the site structure the „Check Modbus devices“ only appears under event console in host parameters. No new datasource program shows up. No new active check appears. Isn’t it possible to create services based on modbus values? I’m new with Check_MK.
Just evaluating if it fits our needs.

···

Hi Dirk,

first you should test if the agent_modbus is working with your device.

If this is working then you should copy the other files in the shown directories under your local structure in your site.

checks → share/check_mk/checks

modbus_value → share/check_mk/checks

wato → share/check_mk/web/plugins/wato

perfometer and checkman are not important for testing

If all went the right way you should find a new rule inside “Datasource programs”.

Best regards

Andreas

Riemekasten Dirk DRiemekasten@natus.de schrieb am Di., 23. Mai 2017 um 16:03 Uhr:

Hi!

I want to monitor our mitsubishi air conditioning system via modbus. How do I activate the modbus from check_mk/share/treasures/modbus? What file has to be copied to which location?
I am using v1.2.8p22.

1 Like