Monitor a UPS Zen-X with a .txt file

Sorry, the Syntax was wrong, I wasn’t using the option which allow me to leave out the useless threshold fields.

Here is the good syntax : echo "P output_voltage voltage=${voltage};185:;150: (In this case : lower than 150 = CRIT, between 185 and 150 = WARN, upper than 185 = OK )

Now I can adapt it to others services, Thank you a lot guys !

Good to hear. Then select your solution and mark this thread as solved.

BR