BrianAdgey
(Brian Adgey)
October 10, 2022, 11:09am
1
CMK version: Checkmk Free Edition 2.1.0p13
OS version: Docker
We have an APC SRV6KIL, which can only be monitored via SNMP using an addon APC APVS9601 SNMP card. APC supply a piece of software which you install on a windows server to monitor the UPS over SNMP, however I would really like to bring everything under one umbrella, and have CheckMK monitor it also. To try to simplify things for now, the card is using SNMP v2, so I only need to provide a public community string. I am hoping ive attached a test made when first setting up the snmp card as a host.
As you can see from the above, it appears to communicate and return data on snmp, however when i rescan to discover services, i only get 2 items back.
The card itself has little to no configuration, and the documentation regarding things like credentials etc is none existent, but from how its setup, it should work, assuming that CheckMK has the relevant mib for it.
I have reviewed:-
Monitoring via SNMP - Monitoring of SNMP devices with Checkmk
and I have also had a look at:
APC PDU monitoring using checkmk raw edition - General - Checkmk Community
Any help would be most appreciated.
Anders
(Anders)
October 10, 2022, 4:49pm
2
Thats one common misunderstandings about Checkmk - It does not rely on MIBs at all. It relies on SNMP checks that you, someone else or tribe needs to write.
If you run a snmp walk on the device what do you get? (first step)
You can also run tcpdump on your target IP to see if snmp walk is working
You can also run a debug check.
BrianAdgey
(Brian Adgey)
October 10, 2022, 6:52pm
4
Thanks for responding. Apologies, I have had to paste the output to the reply as im restricted from attaching files.
.1.3.6.1.2.1.1.1.0 RTCS version 03.02.00
.1.3.6.1.2.1.1.2.0 .0.0
.1.3.6.1.2.1.1.3.0 2493195
.1.3.6.1.2.1.1.4.0
.1.3.6.1.2.1.1.5.0
.1.3.6.1.2.1.1.6.0
.1.3.6.1.2.1.1.7.0 8
.1.3.6.1.2.1.2.1.0 1
.1.3.6.1.2.1.2.2.1.1.1 0
.1.3.6.1.2.1.2.2.1.2.1
.1.3.6.1.2.1.2.2.1.3.1 6
.1.3.6.1.2.1.2.2.1.4.1 1500
.1.3.6.1.2.1.2.2.1.5.1 10000000
.1.3.6.1.2.1.2.2.1.6.1 "60 19 29 10 D7 B0 "
.1.3.6.1.2.1.2.2.1.7.1 1
.1.3.6.1.2.1.2.2.1.8.1 1
.1.3.6.1.2.1.2.2.1.9.1 0
.1.3.6.1.2.1.2.2.1.10.1 10735276
.1.3.6.1.2.1.2.2.1.11.1 118694
.1.3.6.1.2.1.2.2.1.12.1 2680
.1.3.6.1.2.1.2.2.1.13.1 0
.1.3.6.1.2.1.2.2.1.14.1 0
.1.3.6.1.2.1.2.2.1.15.1 0
.1.3.6.1.2.1.2.2.1.16.1 11169564
.1.3.6.1.2.1.2.2.1.17.1 118724
.1.3.6.1.2.1.2.2.1.18.1 6
.1.3.6.1.2.1.2.2.1.19.1 0
.1.3.6.1.2.1.2.2.1.20.1 0
.1.3.6.1.2.1.2.2.1.21.1 0
.1.3.6.1.2.1.2.2.1.22.1 .0.0
.1.3.6.1.2.1.4.1.0 1
.1.3.6.1.2.1.4.2.0 64
.1.3.6.1.2.1.4.3.0 119307
.1.3.6.1.2.1.4.4.0 0
.1.3.6.1.2.1.4.5.0 0
.1.3.6.1.2.1.4.6.0 0
.1.3.6.1.2.1.4.7.0 0
.1.3.6.1.2.1.4.8.0 0
.1.3.6.1.2.1.4.9.0 119307
.1.3.6.1.2.1.4.10.0 118682
.1.3.6.1.2.1.4.11.0 0
.1.3.6.1.2.1.4.12.0 0
.1.3.6.1.2.1.4.13.0 60000
.1.3.6.1.2.1.4.14.0 0
.1.3.6.1.2.1.4.15.0 0
.1.3.6.1.2.1.4.16.0 0
.1.3.6.1.2.1.4.17.0 0
.1.3.6.1.2.1.4.18.0 0
.1.3.6.1.2.1.4.19.0 0
.1.3.6.1.2.1.4.20.1.1.IP REDACTED IP REDACTED
.1.3.6.1.2.1.4.20.1.2.IP REDACTED 1
.1.3.6.1.2.1.4.20.1.3.IP REDACTED 255.255.0.0
.1.3.6.1.2.1.4.20.1.4.IP REDACTED 1
.1.3.6.1.2.1.4.20.1.5.IP REDACTED 65535
.1.3.6.1.2.1.4.21.1.1.0.0.0.0 0.0.0.0
.1.3.6.1.2.1.4.21.1.1.SUBNET REDACTED SUBNET REDACTED
.1.3.6.1.2.1.4.21.1.1.IP REDACTED IP REDACTED
.1.3.6.1.2.1.4.21.1.2.0.0.0.0 1
.1.3.6.1.2.1.4.21.1.2.SUBNET REDACTED 1
.1.3.6.1.2.1.4.21.1.2.IP REDACTED 1
.1.3.6.1.2.1.4.21.1.3.0.0.0.0 0
.1.3.6.1.2.1.4.21.1.3.SUBNET REDACTED 0
.1.3.6.1.2.1.4.21.1.3.IP REDACTED 0
.1.3.6.1.2.1.4.21.1.4.0.0.0.0 0
.1.3.6.1.2.1.4.21.1.4.SUBNET REDACTED 0
.1.3.6.1.2.1.4.21.1.4.IP REDACTED 0
.1.3.6.1.2.1.4.21.1.5.0.0.0.0 0
.1.3.6.1.2.1.4.21.1.5.SUBNET REDACTED 0
.1.3.6.1.2.1.4.21.1.5.IP REDACTED 0
.1.3.6.1.2.1.4.21.1.6.0.0.0.0 0
.1.3.6.1.2.1.4.21.1.6.SUBNET REDACTED 0
.1.3.6.1.2.1.4.21.1.6.IP REDACTED 0
.1.3.6.1.2.1.4.21.1.7.0.0.0.0 GATEWAY REDACTED
.1.3.6.1.2.1.4.21.1.7.SUBNET REDACTED IP REDACTED
.1.3.6.1.2.1.4.21.1.7.IP REDACTED IP REDACTED
.1.3.6.1.2.1.4.21.1.8.0.0.0.0 4
.1.3.6.1.2.1.4.21.1.8.SUBNET REDACTED 3
.1.3.6.1.2.1.4.21.1.8.IP REDACTED 3
.1.3.6.1.2.1.4.21.1.9.0.0.0.0 2
.1.3.6.1.2.1.4.21.1.9.SUBNET REDACTED 2
.1.3.6.1.2.1.4.21.1.9.IP REDACTED 2
.1.3.6.1.2.1.4.21.1.10.0.0.0.0 0
.1.3.6.1.2.1.4.21.1.10.SUBNET REDACTED 0
.1.3.6.1.2.1.4.21.1.10.IP REDACTED 0
.1.3.6.1.2.1.4.21.1.11.0.0.0.0 0.0.0.0
.1.3.6.1.2.1.4.21.1.11.SUBNET REDACTED 255.255.0.0
.1.3.6.1.2.1.4.21.1.11.IP REDACTED 255.255.255.255
.1.3.6.1.2.1.4.21.1.12.0.0.0.0 0
.1.3.6.1.2.1.4.21.1.12.SUBNET REDACTED 0
.1.3.6.1.2.1.4.21.1.12.IP REDACTED 0
.1.3.6.1.2.1.4.21.1.13.0.0.0.0 .0.0
.1.3.6.1.2.1.4.21.1.13.SUBNET REDACTED .0.0
.1.3.6.1.2.1.4.21.1.13.IP REDACTED .0.0
.1.3.6.1.2.1.4.22.1.1.1.IP REDACTED 1
.1.3.6.1.2.1.4.22.1.1.1.GATEWAY REDACTED 1
.1.3.6.1.2.1.4.22.1.2.1.IP REDACTED "00 00 00 00 00 00 "
.1.3.6.1.2.1.4.22.1.2.1.GATEWAY REDACTED "MAC REDACTED "
.1.3.6.1.2.1.4.22.1.3.1.IP REDACTED IP REDACTED
.1.3.6.1.2.1.4.22.1.3.1.GATEWAY REDACTED GATEWAY REDACTED
.1.3.6.1.2.1.4.22.1.4.1.IP REDACTED 3
.1.3.6.1.2.1.4.22.1.4.1.GATEWAY REDACTED 3
.1.3.6.1.2.1.4.23.0 0
.1.3.6.1.2.1.5.1.0 119314
.1.3.6.1.2.1.5.2.0 197
.1.3.6.1.2.1.5.3.0 0
.1.3.6.1.2.1.5.4.0 0
.1.3.6.1.2.1.5.5.0 0
.1.3.6.1.2.1.5.6.0 0
.1.3.6.1.2.1.5.7.0 0
.1.3.6.1.2.1.5.8.0 4161
.1.3.6.1.2.1.5.9.0 0
.1.3.6.1.2.1.5.10.0 0
.1.3.6.1.2.1.5.11.0 0
.1.3.6.1.2.1.5.12.0 0
.1.3.6.1.2.1.5.13.0 0
.1.3.6.1.2.1.5.14.0 4309
.1.3.6.1.2.1.5.15.0 0
.1.3.6.1.2.1.5.16.0 148
.1.3.6.1.2.1.5.17.0 0
.1.3.6.1.2.1.5.18.0 0
.1.3.6.1.2.1.5.19.0 0
.1.3.6.1.2.1.5.20.0 0
.1.3.6.1.2.1.5.21.0 0
.1.3.6.1.2.1.5.22.0 4161
.1.3.6.1.2.1.5.23.0 0
.1.3.6.1.2.1.5.24.0 0
.1.3.6.1.2.1.5.25.0 0
.1.3.6.1.2.1.5.26.0 0
.1.3.6.1.2.1.6.1.0 4
.1.3.6.1.2.1.6.2.0 15
.1.3.6.1.2.1.6.3.0 240000
.1.3.6.1.2.1.6.4.0 0
.1.3.6.1.2.1.6.5.0 0
.1.3.6.1.2.1.6.6.0 0
.1.3.6.1.2.1.6.7.0 0
.1.3.6.1.2.1.6.8.0 0
.1.3.6.1.2.1.6.9.0 0
.1.3.6.1.2.1.6.10.0 0
.1.3.6.1.2.1.6.11.0 0
.1.3.6.1.2.1.6.12.0 0
.1.3.6.1.2.1.6.14.0 0
.1.3.6.1.2.1.6.15.0 0
.1.3.6.1.2.1.7.1.0 114397
.1.3.6.1.2.1.7.2.0 563
.1.3.6.1.2.1.7.3.0 0
.1.3.6.1.2.1.7.4.0 114381
.1.3.6.1.2.1.7.5.1.1.0.0.0.0.161 0.0.0.0
.1.3.6.1.2.1.7.5.1.1.0.0.0.0.41222 0.0.0.0
.1.3.6.1.2.1.7.5.1.1.0.0.0.0.51220 0.0.0.0
.1.3.6.1.2.1.7.5.1.2.0.0.0.0.161 161
.1.3.6.1.2.1.7.5.1.2.0.0.0.0.41222 41222
.1.3.6.1.2.1.7.5.1.2.0.0.0.0.51220 51220
.1.3.6.1.2.1.11.1.0 114376
.1.3.6.1.2.1.11.2.0 114375
.1.3.6.1.2.1.11.3.0 0
.1.3.6.1.2.1.11.4.0 0
.1.3.6.1.2.1.11.5.0 0
.1.3.6.1.2.1.11.6.0 0
.1.3.6.1.2.1.11.8.0 0
.1.3.6.1.2.1.11.9.0 0
.1.3.6.1.2.1.11.10.0 0
.1.3.6.1.2.1.11.11.0 0
.1.3.6.1.2.1.11.12.0 0
.1.3.6.1.2.1.11.13.0 133199
.1.3.6.1.2.1.11.14.0 0
.1.3.6.1.2.1.11.15.0 112172
.1.3.6.1.2.1.11.16.0 113
.1.3.6.1.2.1.11.17.0 0
.1.3.6.1.2.1.11.18.0 0
.1.3.6.1.2.1.11.19.0 0
.1.3.6.1.2.1.11.20.0 0
.1.3.6.1.2.1.11.21.0 1526
.1.3.6.1.2.1.11.22.0 0
.1.3.6.1.2.1.11.24.0 0
.1.3.6.1.2.1.11.25.0 0
.1.3.6.1.2.1.11.26.0 0
.1.3.6.1.2.1.11.27.0 0
.1.3.6.1.2.1.11.28.0 114377
.1.3.6.1.2.1.11.29.0 0
.1.3.6.1.2.1.11.30.0 0
.1.3.6.1.2.1.33.1.1.1.0
.1.3.6.1.2.1.33.1.1.2.0 SRV6KIL
.1.3.6.1.2.1.33.1.1.3.0 456.00DT.I
.1.3.6.1.2.1.33.1.1.4.0 2.0.1
.1.3.6.1.2.1.33.1.1.5.0 9S1939A84574
.1.3.6.1.2.1.33.1.1.6.0
.1.3.6.1.2.1.33.1.2.1.0 2
.1.3.6.1.2.1.33.1.2.2.0 0
.1.3.6.1.2.1.33.1.2.3.0 65535
.1.3.6.1.2.1.33.1.2.4.0 100
.1.3.6.1.2.1.33.1.2.5.0 2732
.1.3.6.1.2.1.33.1.2.6.0 40
.1.3.6.1.2.1.33.1.2.7.0 27
.1.3.6.1.2.1.33.1.3.1.0 0
.1.3.6.1.2.1.33.1.3.2.0 1
.1.3.6.1.2.1.33.1.3.3.1.2.1 499
.1.3.6.1.2.1.33.1.3.3.1.3.1 247
.1.3.6.1.2.1.33.1.3.3.1.4.1 0
.1.3.6.1.2.1.33.1.3.3.1.5.1 0
.1.3.6.1.2.1.33.1.4.1.0 3
.1.3.6.1.2.1.33.1.4.2.0 498
.1.3.6.1.2.1.33.1.4.3.0 1
.1.3.6.1.2.1.33.1.4.4.1.2.1 229
.1.3.6.1.2.1.33.1.4.4.1.3.1 48
.1.3.6.1.2.1.33.1.4.4.1.4.1 0
.1.3.6.1.2.1.33.1.4.4.1.5.1 15
.1.3.6.1.2.1.33.1.5.1.0 499
.1.3.6.1.2.1.33.1.5.2.0 1
.1.3.6.1.2.1.33.1.5.3.1.2.1 247
.1.3.6.1.2.1.33.1.5.3.1.3.1 0
.1.3.6.1.2.1.33.1.5.3.1.4.1 0
.1.3.6.1.2.1.33.1.6.1.0 0
.1.3.6.1.2.1.33.1.7.1.0 .0.0
.1.3.6.1.2.1.33.1.7.2.0 0
.1.3.6.1.2.1.33.1.7.3.0 6
.1.3.6.1.2.1.33.1.7.4.0
.1.3.6.1.2.1.33.1.7.5.0 0
.1.3.6.1.2.1.33.1.7.6.0 0
.1.3.6.1.2.1.33.1.8.1.0 1
.1.3.6.1.2.1.33.1.8.2.0 -1
.1.3.6.1.2.1.33.1.8.3.0 -1
.1.3.6.1.2.1.33.1.8.4.0 -1
.1.3.6.1.2.1.33.1.8.5.0 2
.1.3.6.1.2.1.33.1.9.1.0 0
.1.3.6.1.2.1.33.1.9.2.0 0
.1.3.6.1.2.1.33.1.9.3.0 0
.1.3.6.1.2.1.33.1.9.4.0 0
.1.3.6.1.2.1.33.1.9.5.0 6000
.1.3.6.1.2.1.33.1.9.6.0 0
.1.3.6.1.2.1.33.1.9.7.0 0
.1.3.6.1.2.1.33.1.9.8.0 0
.1.3.6.1.2.1.33.1.9.9.0 0
.1.3.6.1.2.1.33.1.9.10.0 0
.1.3.6.1.2.1.33.13.1.0 999999999
.1.3.6.1.2.1.33.13.2.0 999999999
.1.3.6.1.2.1.33.13.3.0 999999999
.1.3.6.1.2.1.33.13.4.0 0
.1.3.6.1.2.1.33.13.5.0 0
.1.3.6.1.2.1.33.13.6.0 0
.1.3.6.1.2.1.33.13.7.0 0
.1.3.6.1.4.1.21111.1.1.1.1.0
.1.3.6.1.4.1.21111.1.1.1.2.0 68
.1.3.6.1.4.1.21111.1.1.13.1.0 999999999
.1.3.6.1.4.1.21111.1.6.1.1.0
.1.3.6.1.4.1.21111.1.6.1.2.0 68
.1.3.6.1.4.1.21111.1.6.1.3.0 SRV6KIL
.1.3.6.1.4.1.21111.1.6.1.4.0 9S1939A84574
.1.3.6.1.4.1.21111.1.6.1.5.0 "FF FF FF FF FF FF FF FF FF FF FF FF FF FF FF FF FF FF FF FF FF FF FF FF FF FF FF FF FF FF FF "
.1.3.6.1.4.1.21111.1.6.1.6.0 456.00DT.I
.1.3.6.1.4.1.21111.1.6.1.7.0 UPS-IDEN
.1.3.6.1.4.1.21111.1.6.2.1.0 230
.1.3.6.1.4.1.21111.1.6.2.2.0 230
.1.3.6.1.4.1.21111.1.6.2.3.0 500
.1.3.6.1.4.1.21111.1.6.2.4.0 26
.1.3.6.1.4.1.21111.1.6.2.5.0 6000
.1.3.6.1.4.1.21111.1.6.2.6.0 2400
.1.3.6.1.4.1.21111.1.6.3.1.0 2
.1.3.6.1.4.1.21111.1.6.3.2.0 -1
.1.3.6.1.4.1.21111.1.6.3.3.0 65535
.1.3.6.1.4.1.21111.1.6.3.4.0 1000
.1.3.6.1.4.1.21111.1.6.3.5.0 2732
.1.3.6.1.4.1.21111.1.6.3.6.0 40
.1.3.6.1.4.1.21111.1.6.3.7.0 270
.1.3.6.1.4.1.21111.1.6.3.8.0 0
.1.3.6.1.4.1.21111.1.6.3.9.0 2
.1.3.6.1.4.1.21111.1.6.4.1.0 0
.1.3.6.1.4.1.21111.1.6.4.2.0 0
.1.3.6.1.4.1.21111.1.6.4.3.0 0
.1.3.6.1.4.1.21111.1.6.4.4.0 1
.1.3.6.1.4.1.21111.1.6.4.5.1.1.1 1
.1.3.6.1.4.1.21111.1.6.4.5.1.2.1 499
.1.3.6.1.4.1.21111.1.6.4.5.1.3.1 2471
.1.3.6.1.4.1.21111.1.6.4.5.1.4.1 0
.1.3.6.1.4.1.21111.1.6.4.5.1.5.1 0
.1.3.6.1.4.1.21111.1.6.4.5.1.6.1 0
.1.3.6.1.4.1.21111.1.6.4.5.1.7.1 0
.1.3.6.1.4.1.21111.1.6.4.5.1.8.1 0
.1.3.6.1.4.1.21111.1.6.5.1.0 3
.1.3.6.1.4.1.21111.1.6.5.2.0 4980
.1.3.6.1.4.1.21111.1.6.5.3.0 170
.1.3.6.1.4.1.21111.1.6.5.4.0 0
.1.3.6.1.4.1.21111.1.6.5.5.0 0
.1.3.6.1.4.1.21111.1.6.5.6.0 1
.1.3.6.1.4.1.21111.1.6.5.7.1.1.1 1
.1.3.6.1.4.1.21111.1.6.5.7.1.2.1 2293
.1.3.6.1.4.1.21111.1.6.5.7.1.3.1 48
.1.3.6.1.4.1.21111.1.6.5.7.1.4.1 0
.1.3.6.1.4.1.21111.1.6.5.7.1.5.1 0
.1.3.6.1.4.1.21111.1.6.5.7.1.6.1 0
.1.3.6.1.4.1.21111.1.6.5.7.1.7.1 150
.1.3.6.1.4.1.21111.1.6.5.7.1.8.1 0
.1.3.6.1.4.1.21111.1.6.5.8.0 1
.1.3.6.1.4.1.21111.1.6.5.9.0 08000001
.1.3.6.1.4.1.21111.1.6.6.1.0 499
.1.3.6.1.4.1.21111.1.6.6.2.0 1
.1.3.6.1.4.1.21111.1.6.6.3.1.1.1 1
.1.3.6.1.4.1.21111.1.6.6.3.1.2.1 2471
.1.3.6.1.4.1.21111.1.6.6.3.1.3.1 0
.1.3.6.1.4.1.21111.1.6.6.3.1.4.1 0
.1.3.6.1.4.1.21111.1.6.7.1.0 0
.1.3.6.1.4.1.21111.1.6.7.2.0 6
.1.3.6.1.4.1.21111.1.6.7.3.0
.1.3.6.1.4.1.21111.1.6.7.4.0 0
.1.3.6.1.4.1.21111.1.6.8.1.0 0
.1.3.6.1.4.1.21111.1.6.8.2.0 0
.1.3.6.1.4.1.21111.1.6.8.3.0 0
.1.3.6.1.4.1.21111.1.6.8.4.0 1
.1.3.6.1.4.1.21111.1.6.8.5.0 0
.1.3.6.1.4.1.21111.1.6.8.6.0 0
.1.3.6.1.4.1.21111.1.6.9.1.0 10/10/2022 17:44:46
.1.3.6.1.4.1.21111.1.6.10.1.0 2400
.1.3.6.1.4.1.21111.1.6.10.2.0 1
.1.3.6.1.4.1.21111.1.6.10.3.0 0
.1.3.6.1.4.1.21111.1.6.10.4.0 0
.1.3.6.1.4.1.21111.1.6.10.5.0 0
.1.3.6.1.4.1.21111.1.6.11.1.0 1
.1.3.6.1.4.1.21111.1.6.11.2.0 0
.1.3.6.1.4.1.21111.1.6.11.3.0 2
.1.3.6.1.4.1.21111.1.6.11.4.0 1
.1.3.6.1.4.1.21111.1.6.11.5.0 0
.1.3.6.1.4.1.21111.1.6.11.6.0 0
.1.3.6.1.4.1.21111.1.6.11.7.0 2
.1.3.6.1.4.1.21111.1.6.11.8.0 2
.1.3.6.1.4.1.21111.1.6.11.9.0 0
.1.3.6.1.4.1.21111.1.6.11.10.0 2
.1.3.6.1.4.1.21111.1.6.11.11.0 0
.1.3.6.1.4.1.21111.1.6.11.12.0 0
.1.3.6.1.4.1.21111.1.6.11.13.0 0
.1.3.6.1.4.1.21111.1.6.11.14.0 540
.1.3.6.1.4.1.21111.1.6.11.15.0 460
.1.3.6.1.4.1.21111.1.6.11.16.0 241
.1.3.6.1.4.1.21111.1.6.11.17.0 219
.1.3.6.1.4.1.21111.1.6.11.18.0 1
.1.3.6.1.4.1.21111.1.6.11.19.0 09/05/17
.1.3.6.1.4.1.21111.1.6.11.20.0 7
.1.3.6.1.4.1.21111.1.6.11.21.0
.1.3.6.1.4.1.21111.1.6.11.22.0 410TLN
.1.3.6.1.4.1.21111.1.6.11.23.0 20
.1.3.6.1.4.1.21111.1.6.11.24.0 43020180300600
.1.3.6.1.4.1.21111.1.6.11.25.0 0
.1.3.6.1.4.1.21111.1.6.11.26.0 43000060180300
.1.3.6.1.4.1.21111.1.6.11.27.0 43265242253276
.1.3.6.1.4.1.21111.1.6.11.28.0 43196184173161
.1.3.6.1.4.1.21111.1.6.12.998.0
.1.3.6.1.4.1.21111.1.6.13.1.0 999999999
.1.3.6.1.4.1.21111.1.6.13.2.0 999999999
.1.3.6.1.4.1.21111.1.6.13.3.0 999999999
.1.3.6.1.4.1.21111.1.6.13.4.0 0
.1.3.6.1.4.1.21111.1.6.13.5.0 0
.1.3.6.1.4.1.21111.1.6.13.6.0 0
.1.3.6.1.4.1.21111.1.6.13.7.0 0
The above appears to show its outputting data. Any help really appreciated.
All OIDs starting with “.1.3.6.1.2.1.33” is generic UPS information. This looks good.
But this is the reason why the device is not correctly recognized by CMK.
Inside “.1.3.6.1.2.1.1.2.0” (SysObjectID) you should see a value the can identify the device.
CMK expects at the moment one on the following values there.
DETECT_UPS_GENERIC = any_of(
equals(".1.3.6.1.2.1.1.2.0", ".1.3.6.1.4.1.232.165.3"),
equals(".1.3.6.1.2.1.1.2.0", ".1.3.6.1.4.1.476.1.42"),
equals(".1.3.6.1.2.1.1.2.0", ".1.3.6.1.4.1.534.1"),
equals(".1.3.6.1.2.1.1.2.0", ".1.3.6.1.4.1.935"),
equals(".1.3.6.1.2.1.1.2.0", ".1.3.6.1.4.1.8072.3.2.10"),
equals(".1.3.6.1.2.1.1.2.0", ".1.3.6.1.4.1.12551.4.0"),
startswith(".1.3.6.1.2.1.1.2.0", ".1.3.6.1.2.1.33"),
startswith(".1.3.6.1.2.1.1.2.0", ".1.3.6.1.4.1.5491"),
startswith(".1.3.6.1.2.1.1.2.0", ".1.3.6.1.4.1.705.1"),
startswith(".1.3.6.1.2.1.1.2.0", ".1.3.6.1.4.1.818.1.100.1"),
This detect function needs to be extended with the following line
startswith(".1.3.6.1.2.1.1.1.0", "RTCS version"),
But pay attention this “RTCS” string has nothing to do with the device as UPS. It looks more like the type of an small controller chip like an ESP.
BrianAdgey
(Brian Adgey)
October 11, 2022, 7:59am
7
I am really sorry, I am a complete noob when it comes to CMK, I literally started using it the end of last week. Are you saying that the snmp info that is coming from the management card doesn’t provide any data related to the ups? I dont suppose you could point me in the right direction as to what i need to change to add this line, and is that going to result in me receiving monitoring data from the ups?
Your device provides the information for UPS but it cannot be identified as UPS automatically by CMK.
The CMK systems works the following way.
fetch “.1.3.6.1.2.1.1.1.0” and “.1.3.6.1.2.1.1.2.0”
compare this value to the value requested by every check
try to discover checks that match the fetched values
As your device provides no correct information on this OIDs it is not possible for CMK to find the UPS checks on your system automatically.
With version 2.1 and SNMP devices without correct SysDescrOID it is not so easy to discover services.
BrianAdgey
(Brian Adgey)
October 11, 2022, 8:47am
10
Thanks, I get that aspect of it, its what I need to edit or add to add the values to compare that im clueless about. I dont suppose you could point me in the right direction, whether it be a link to the relevant article or path to a file etc.
BrianAdgey
(Brian Adgey)
October 13, 2022, 2:06pm
11
Thanks again for the info. Any chance you could point me to the files that contain the data you referred to that i need to modify to get this over the line?
Many thanks,
The file you need to modify is
~/lib/check_mk/base/plugins/agent_based/utils/ups.py
But pay attention if you modify this file you need to make the modification again after the next CMK update.
Worked here, but it only retrieved two more services Battery Capacity and Battery State.
system
(system)
Closed
November 1, 2023, 1:02pm
14